There is no requirement for a separate EGC from, the emergency disconnect to the main service panel, the neutral serves that purpose when you bond the neutral bus to the ground bus at the main service panel, with the main overcurrent device.But unfortunately no egc from em-cum-service equipment!
The circuit conductors between the emergency disconnect and the main service disconnect are treated as service entrance conductors
and the establishment of a separate ground bus only occurs after the main service overcurrent device.
Only after that main service overcurrent device, do the neutral and the grounding system conductors become separate and isolated from each other.
The emergency disconnect would also have a bond connection between the neutral bus and the enclosure ground bus, to serve the purpose of handling ground fault currents in the emergency disconnect, If it lacks a factory neutral to ground connection.