I believe a splice/disconnect, like you describe, could impact the performance of the SPD, which usually want shortest possible leads with as little bending as possible (90°bends are a definite non-no).
2023 NEC
Regarding..........." if your panel takes a hit and destroys the SPD........'
That shouldn't happen if the SPD is rated for the fault current available as per 242.8
Short Circuit Current Rating. "The SPD shall be marked with a short-circuit current rating and shall not be installed at a point on the system where the available fault current is in excess of that rating."
Does anyone or the installer know what the fault current was? I really doubt it.
NEC
Commentary found in Article 100 indicates for a typical one family dwelling example with a 100 amp service supplied by a 37.5 kilovolt ampere transformer......at a distance of 25 feet, ........the available short circuit would be approximately 6,000 amperes.
A type one SPD is usually found at the service,242.13 (A) (B).
The commentary example is perhaps somewhat extreme inasmuch as the distance was only 25 feet and considering other given parameters.
Of course it is a fact that the closer / further distance is what will determine the impact on the amount of short circuit current available.
Please read on: It's worth your time.
Some say I am too involved in the
Code to know what really goes on in the real world. I have a lot to say about that, so take the time to read the facts from the 2012 Edition
NFPA 70E Standard for Electrical Safety in the Workplace.
Well, I have heard from a few licensed electricians who say that they should have been more involved considering how destructive it can be when short circuit currents explode in or near your body, especially your eyes while working on any energized equipment.
Here's a few real time facts about about what actually happens while working on energized equipment and suddenly you fumble your screw driver or other tool and create a phase to ground or phase -to- phase short. Some have been edited.
From the
2012 Edition of NFPA 70 E Informative Annex K General Categories of Electrical Hazards
K.2 Electric Shock. The current required to light a 7.5 watt, 129 volt lamp, if passed across the chest, is enough to cause a fatality. Affecting especially the lungs, heart, and brain. And that may be depending on how healthy you are.
K.3 Arc Flash. When an electric current passes through air between ungrounded conductors or between ungrounded and grounded conductors, the temperature can reach35,000 degrees Fahrenheit. Scientist say that's about 7 times hotter than the surface of the sun. Arc flashes can and do kill at distances of 10 feet. You can't outrun it.
K.4 Arc Blast. ."....can melt coper conductors, when it turns from a solid to a vapor. Knock workers off of ladders, rupturing ear-drums and collapsing your lungs. Molten metal is expelled away from the arc at speeds exceeding700 MPH fast enough for shrapnel to completely penetrate the human body."
Thanks for reading
Comments accepted