To vendors, electricians, engineers,
For a house with 10 GFCI receptacles, they would be useless if the GFCIs got fried by external surges. The internal MOV (Metal Oxide Varistors) in each is not enough. They are good for only a few years then the GFCI circuit become vulnerable to damage.
Now consider this Siemens whole house 140,000A surge current SPD (Surge Protector Device) with data sheet at:
https://www.downloads.siemens.com/d...aspx?pos=download&fct=getasset&id1=BTLV_43434
available at amazon https://www.amazon.com/gp/product/B013WINMK6/ref=ask_ql_qh_dp_hza
The wires are only size #10 AWG and it requires 20A breaker.
What would happen if this is connected to the main breaker of say 100A instead of buying 16 pieces and connecting to each 20A breaker.
Note it is not an appliance. It doesn't conduct at normal voltage. Only when it reaches above the threshold voltage (MCOV rating) that it begins to conduct and do the voltage divider impedance action thing. But notice that this voltage divider action is only for the surges, not the normal 100A current.
So my question is whether Siemens requiring it to put on each 20A breaker and buy 16 pieces is just sales gimmick instead of buying just one to put on the main 100A breaker.
Can the 100A regular current really passes through the Siemens SPD when the SPD only conducts at higher voltage during actual surges. Even then, the voltage divider action is for only for the surge current and not the regular 100A, is it?
Btw.. let's not confuse the 140,000A surge current rating which is the capacity of the Surge current the SPD can handle, not the regular current (note too that Siemens knows their #10 awg can handle 140,000A surge current because it is not continuous.. so what's wrong putting it in 100A breaker instead of buying 16 pieces for each 20A breakers?).
If you want to protect all the 10 GFCI receptacles at the house, what kind of main breaker SPD do you usually use? Do you really need the SPD to have #2 AWG wire. Notice an SPD is not normal load or appliance so why does the wiring have to match the regular wiring and ampere table?
For a house with 10 GFCI receptacles, they would be useless if the GFCIs got fried by external surges. The internal MOV (Metal Oxide Varistors) in each is not enough. They are good for only a few years then the GFCI circuit become vulnerable to damage.
Now consider this Siemens whole house 140,000A surge current SPD (Surge Protector Device) with data sheet at:
https://www.downloads.siemens.com/d...aspx?pos=download&fct=getasset&id1=BTLV_43434
available at amazon https://www.amazon.com/gp/product/B013WINMK6/ref=ask_ql_qh_dp_hza
The wires are only size #10 AWG and it requires 20A breaker.
What would happen if this is connected to the main breaker of say 100A instead of buying 16 pieces and connecting to each 20A breaker.
Note it is not an appliance. It doesn't conduct at normal voltage. Only when it reaches above the threshold voltage (MCOV rating) that it begins to conduct and do the voltage divider impedance action thing. But notice that this voltage divider action is only for the surges, not the normal 100A current.
So my question is whether Siemens requiring it to put on each 20A breaker and buy 16 pieces is just sales gimmick instead of buying just one to put on the main 100A breaker.
Can the 100A regular current really passes through the Siemens SPD when the SPD only conducts at higher voltage during actual surges. Even then, the voltage divider action is for only for the surge current and not the regular 100A, is it?
Btw.. let's not confuse the 140,000A surge current rating which is the capacity of the Surge current the SPD can handle, not the regular current (note too that Siemens knows their #10 awg can handle 140,000A surge current because it is not continuous.. so what's wrong putting it in 100A breaker instead of buying 16 pieces for each 20A breakers?).
If you want to protect all the 10 GFCI receptacles at the house, what kind of main breaker SPD do you usually use? Do you really need the SPD to have #2 AWG wire. Notice an SPD is not normal load or appliance so why does the wiring have to match the regular wiring and ampere table?