HMMM... in the US or Europe, might work. In Jamaica... we cannot even get accurate hurricane reports on the weather alerts... lol.
HMMM... in the US or Europe, might work. In Jamaica... we cannot even get accurate hurricane reports on the weather alerts... lol.
When a MOV (metal oxide varistor) is near end of life (from many small surge strikes over span of time), it would conduct at lower and lower voltage until it can even conduct with regular voltage say 120v (from the MCOV of 150v), then it would go into thermal runaway (burn) because of the continuous conduction. Can anyone give example of any 120v GFCI receptacle with burnt MOV. Doesn't it burn the entire receptacle since the housing is plastic?
HMMM... in the US or Europe, might work. In Jamaica... we cannot even get accurate hurricane reports on the weather alerts... lol.
When MOV fails at more than four times it's rated JOULES, it explodes or vaporizes. No conduction occurs when this happens because after explosion it is reduced to small pieces.
The case is made of high temperature molded ceramics—not plastic.
This feature is used to gain approval from UL because they are exposed to high temperature measured in joules.
During it's lifespan, it safely dissipates the heat caused by spikes. UL 1449 approves MOVs that safely dissipate energy to ground at rated joules below the safe limit.
In other words, if it fails within their set benchmark—it is good and approval follows.
However, there is a problem with this practice.
Not all surges are created equal. In order to have effective protection, you would need multiple arrangement of MOVs that will handle all levels of surges and different installation techniques of electricians who are going to implement this (supposedly) “life-saving” protection.
Some surges even emanate locally-- that is-- inside the house. Relays going off and on, motors, transformers etc.
Electricians know what MOV does. . . but that knowledge is not enough.
Electrical concepts are too complex and learning the technology is far more important than simply knowing how they work.
Only through this rounded knowledge can we have a reliable fault-proof SPD that will benefit consumer--and not being used by insurance companies as cow cash like others had been snivelling about.
.
Can anyone give example of any 120v GFCI receptacle with burnt MOV. Doesn't it burn the entire receptacle since the housing is plastic?
Not a receptacle, but I have seen several power strips burn up like a Roman candle. One right before my eyes. I believe we had a discussion here several years ago about the cause of a fire. It was clear from the picture that a power strip that was shoved under a desk which powered a computer and other equipment was the cause of a fire that destroyed the whole room.
Here in this country with our grounded receptacles, you cannot use a surge protector on the load side of a GFCI receptacle or a circuit protected by a GFCI breaker. This is because the MOVs are from each side to ground and the normal transients that occur will cause conduction from hot to ground and cause the GFCI device to nuisance trip.
-Hal
How about drilling a carefully-placed hole through the extender that lines up with the reset button, and installing a plastic push rod through it?. . . I have to pull the whole thing out to expose the buttons on the receptacle to reset it.
How about drilling a carefully-placed hole through the extender that lines up with the reset button, and installing a plastic push rod through it?
The UL product standard was already changed to increase the amount of surge protection within the GFCI itself, but there is limited space in the device. Not sure anything more can be done with the device itself.
The GFCIs are already required to be self-testing, but they are not required to fail open..they are permitted to fail open, or indicate failure using an audible and/or visual alarm. I guess they could change UL 943 an require a fail open device and leave the surge protection up to the owner. Not sure about AFCIs as far as self testing.... let the surge destroy the GFCI but make it fail-open so that it will be obvious it needs to be replaced. ...
-Hal
![]()