“FirstSurgeTM is GRM-equipped notifying you a rare safety hazard exists due to a compromised electrical system neutral to ground bond. What will you see and hear when this occurs?
Audible Alarm: Beeps Green LED(s): Remains Lit Red Service Light: Flashes”
What will those millions do when this device detects they have no neutral to ground bond?

I already had one unit in my other building. About 5 months ago. A veteran US electrical engineer taught me about it and convinced me its compatible in my black to red line to line 240v system where each phase is 120v relative to ground (grounded centertapped).
If you connect the ground and neutral of the Siemens First Surge together, it won't sound any alarm even if they are not connected to the bus bar (just like the above fully energized with normal "ok" green lights on and no other warning alarms). The above was just temporary just for testing and only file photo. They need to be connected to bus bar to activate all protection modes, L-L, L-G, N-G fault. Note all connections were done by qualified skilled electricians.
Also all SPDs have thermal fuse to limit the burning of the MOVs. The ones in GFCI receptacle don't have thermal fuse. Also in the US. Your MOV inside GFCI receptacle is connected L to N. In our case, it's connected L-L so the MOV can reach end of life faster than yours. Hence need more protection.