BTW there are 90 tracks wired in this manner.
I will make some assumptions.
90 tracks does not sound like a dwelling and if its commercial there are likely suspended ceilings, I also assume the wiring is concealed. 250 watts is beyond the ability of a class 2 power source.
That being the case;
411.4(A)(1) will require a Chapter 3 wiring method. (Pipe and wire, NM or MC cables etc.)
334.12(A)(2) prohibits using NM assuming commercial and a dropped ceiling
So this leaves you with pipe and wire or MC, running 4 AWG MC will get kind of expensive. :grin:
If it where me, I would look into moving the transformers right next to the loads, in that way you could run 12/2 MC line voltage to each transformer without having severe voltage drop problems. Then your secondaries would be very short and 10 AWG would be fine.
If you have the time take a look at the instructions that come with a low volt lighting transformer, I think you will be very surprised at the required wire sizes due to voltage drop. When your only dealing with 12 volts to start with voltage drop is a real issue that results in greatly reduced light output.
Physics exposes Ignorance!:grin: