Certainly the rules as written do not distinguish. But the reasoning behind those rules goes in this order:continuous load is the driving element behind both conductor and CB sizing, per NEC
- A non-100% rated breaker may nuisance trip at a continuous load exceeding 80% of its rating (not an immediate safety issue, but a problem).
- Therefore the breaker needs to be increased in size by a 25% factor. Now the conductors are no longer protected properly (a safety issue).
- Therefore the conductors get increased in ampacity .by a 25% factor as well.
You are missing the point of scenario (B), the load is 1000A continuous in all scenarios. There is no safety issue (overloading/overheating anything), other than the breaker tripping when we don't want it to, and whatever knock-on effects that could have.
And as a practical matter, in mild ambient temperatures, in not heavily loaded panels, a breaker may hold indefinitely at its nameplate rating. In which case there would be nothing wrong with scenario (B). It is simply the uncertainty as to whether the breaker would hold that causes the NEC to prohibit scenario (B).
And that's all a 100% rated breaker is--a breaker alone in an enclosure designed to ensure that it doesn't trip below 100% of its rating under continuous loading conditions. In free air, at 40C ambient, all breakers are tested to hold continuously at 100% of their rating.
Cheers, Wayne