You can not get 120/240 out of a wyecharlie b,
You are showing a Delta, but ideally the XFMR output, especially where it is 120/240 or 120/208 is a Y not Delta, so load can always be balanced.
Cheers!
TBNK
If the wye is 208 line to line then all lines will be 120 to neutral.
If the wye were 240 line to line then all lines to neutral will be 138.5 volts.
240 volt delta with the midpoint of one phase grounded will have 120/240 across that phase, it will have 208 volts from midpoint to opposite corner of the delta.
You can't change those ratios unless you change the angles of corners of the triangle - and doing that will change lengths of sides and they will no longer all be equal leaving you with unequal line to line voltages if you designed a transformer that way. Similar result changing angles or lengths of the vectors forming the "wye".