Are you using the side screws with the "push-in" connections? If so that is in compliance with the UL listing, but it is something that I would never do. If you are using the back "screw actuated clamp terminals and putting additional wires under the side screw, you are not in compliance with the listing information.Single and duplex receptacles rated 15 and 20 A that are provided with more than one set of terminals for the connection of line and neutral conductors have been investigated to feed branch circuit conductors connected to other outlets on a multi-outlet branch circuit, as follows:
Back wire (screw actuated clamp type) terminations with multiple wire access holes used concurrently to terminate more than one conductor
Side wire (binding screw) terminals used concurrently with their respective push-in (screwless) terminations to terminate more than one conductor
Single and duplex receptacles rated 15 and 20 A that are provided with more than one set of terminals for the connection of line and neutral conductors have not been investigated to feed branch circuit conductors connected to other outlets on a multi-outlet branch circuit, as follows:
Side wire (binding screw) terminal with its associated back wire (screw actuated clamp type) terminal
Multiple conductors under a single binding screw
Multiple conductors in a single back wire hole
Are you using the side screws with the "push-in" connections? If so that is in compliance with the UL listing, but it is something that I would never do.
I used to believe the same thing, but where I work now we back stab. The time it saves is unbelievable and it will more than pay for itself on the rare occasion we need to replace one. If you strip the wires properly and check to make sure the stab grabs you have very few that fail."stabbing outlets" is a guaranteed service call at a later date.
I guess I am a "wrapper". I have wasted too much time chasing down lost nuetrals because of back stabbed connections.Some are 'stabbers'
Some are 'wrappers'
I'll take that bet!I'll lay money I can strip, loop and terminate within 10 seconds of your quick wire method.
OK, that's 500 seconds in a house with 50 devices. A whopping 8 minutes
Jim, just F.Y.I. BINNEY is not BENNY.Originally posted by jimwalker:
And glad to see your still with us.
What do you do when adding to or reparing an existing circuit that is wired with 14 gauge wire? Do you mix 12 and 14 on the same circuit? This is clearly inappropriate and I wouldn't let you do get away with it in my house.Originally posted by tim:
We don't buy any 14 gage wire. 12 is the only way to go. I use to back stab all the time. Since you can't stab 12 anymore, we have gotten use to wrapping. Don't shove it into me when you can wrap me and be snug. (OUCH) Tim