Can't protect the receptacle with a breaker larger than its rating.
210.21 Outlet Devices. Outlet devices shall have an ampere
rating that is not less than the load to be served and shall
comply with 210.21(A) and (B).
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A
single receptacle installed on an individual branch circuit shall
have an ampere rating not less than that of the branch circuit.
(3) Receptacle Ratings. Where connected to a branch circuit
supplying two or more receptacles or outlets, receptacle ratings
shall conform to the values listed in Table 210.21(B)(3), or,
where rated higher than 50 amperes, the receptacle rating shall
not be less than the branch-circuit rating.
Edit: this is from 2017 because I have a searchable pdf of it. I doubt these sections have changed.