HI, I need code references for reasons not to use spider boxes as permanent power (currently wanted for outside). Can anyone direct me to this?
Not necessarily, it could be used under 525 for fairgrounds.A Spider box is considered temporary wiring and thus must meet article 590 and this includes 590.3 that it is one limited to 90 days duration.
Since it it being used as permanent power and is supplied by a cord, that makes the supply cord a violation of 400.12(1).HI, I need code references for reasons not to use spider boxes as permanent power (currently wanted for outside). Can anyone direct me to this?
fairs and carnivals by their nature are temporary.Not necessarily, it could be used under 525 for fairgrounds.
Infinity and I had the same thought. And if it's being removed every so often, even for a day, it's no longer in continuous use.
Wow, that's a really nice buuuuh...enclosure. Yeah, enclosure.Spider Box
View attachment 2578397
My immediate thought exactly. Can't be used in lieu of permanent wiring.Since it it being used as permanent power and is supplied by a cord, that makes the supply cord a violation of 400.12(1).
If you look at the Southwire description for the similar product, it says:As in a temporary recept bundle on a cord? It's temporary, also it has no way of being covered while in-use, also it's on a cord.... maybe I'm thinking of something else though...
You have to use the proper matching Hubbell watertight plugs on your cables.If you look at the Southwire description for the similar product, it says:
I would agree, that this configuration is not water proof while in use, yet the misleading description would lead one to indicate that it is.
- WATERPROOF FEATURES: Designed for use in wet or rainy conditions, this box is rated NEMA-3 for rainproof durability, ensuring safety with all outlets equipped with waterproof covers
I am reading permanent as being installed and believe when you install the spider box as opposed to just letting it set as intended, the supply becomes permanent wiring and you can't supply it with a cord.1) Even if this is permanent, I am not sure that 400.12(1) applies. If I have a receptacle on an outside wall, a spiderbox with an inlet some distance outside, and a cord between them, I don't see that as the cord being used in place of the fixed wiring of a structure. It is _outside_ (not part of a structure), and can clearly be quickly replaced (not fixed).
2) A spiderbox is a pretty generic term, and could certainly include devices designed to be 'waterproof in use'.
-Jonathan