splice in panel box

Status
Not open for further replies.

SheppardJ

Member
Location
Tallahassee,FL
Can anyone tell me where in the code it says the proper way spice a wire in a panel? One of my electricians de-rated a #4 aluminum to a #10 copper so it would fit under a breaker with a split bolt and wrapped it with black tape thoroughly. A home inspector is saying it is a code violation even though the inspector had no problem with it. Home inspector says it must be wrapped in a double layer of heat shrink.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Ask the HI to show you where he came up with his statement.

In the meantime read 110.3(B) and all of 110.14

Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Split bolts have been taped for a hundred years with varying methods from rubber tape covered in friction tape to plastic tape to Scotch Pads. You can also use a plastic cover to insulate the connection like below and forget the tape altogether. I would guess that the person inspecting the connection would need to determine if it is adequately insulated.


http://ecat.burndy.com/Comergent/burndy/cat/611322

UCT_COVER_OPEN.jpg
 

SheppardJ

Member
Location
Tallahassee,FL
H.I.

H.I.

Thank for the info. I'm not sure he could tell me where he found it. He also put that he didn't understand why there where no main breakers in the 2 panels "the homeowner and I finally found it outside on the meter" brilliant! Seems like these guys just love to scare homeowners.
 

user 100

Senior Member
Location
texas
Seems like these guys just love to scare homeowners.

I think that with a lot of them it's more ignorance than anything else and they need to learn that just because they are unfamiliar/uncomfortable with a certain practice that doesn't mean that practice is wrong/dangerous or "against code".

He may be concerned about future failure of the tape job, but if it was done correctly, its fine- we have many, many failure-free examples that were taped up decades ago.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
There was a period of time back in the Eighties when my local electrical inspectors would occasionally gig me for wire nutting a few branch circuit conductors when doing a service upgrade in the existing location. I would have pigtailed an additional length of wire with a wire nut for a legacy branch circuit conductor.

The inspector was misreading the section on cross sectional area fill for the open space between the breaker assembly and the metal can. The Code language was easy to misinterpret back then.

I still have amateurs question whether any splicing can be done in electrical breaker boxes to this day. The HI community is so fraught with claims of fact based solely upon what someone says they "heard" that it gets really frustrating. . .
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
HI's are not code inspectors and should not be giving code references. In fact in many cases they're prohibited from doing so by their SOP. It sounds like in evaluating the splice mentioned in the OP the HI was giving his opinion which is what they're supposed to do. Having seen no evidence of what this splice actually looks like it's hard to say if he was correct or not.
 

kwired

Electron manager
Location
NE Nebraska
If a HI sees something he doesn't know anything about or understand, but still has concerns over he should make a note that it needs checked out by someone that is qualified to determine it's condition. They should not be saying it is wrong or is a hazard, or saying that it is safe either.

Situation like the OP has may possibly be a case where they make a note of what was seen and consult some other qualified person before proceeding with a report, he may find out that tape is considered acceptable insulation for a split bolt connection and mark that questionable item off his list.
 

Cavie

Senior Member
Location
SW Florida
Thank for the info. I'm not sure he could tell me where he found it. He also put that he didn't understand why there where no main breakers in the 2 panels "the homeowner and I finally found it outside on the meter" brilliant! Seems like these guys just love to scare homeowners.

Many of them are DA's that have authority over this they know nothing about. They read a book.
 
Status
Not open for further replies.
Top