Splice in Service Panel

Status
Not open for further replies.
Can you have a splice in the service panel?

Say you run a circuit and the wire is 4 or 5" short...can you splice onto it to make it long enough to reach ...whatever?
 
Thank you so much!

So the service panel is the same as a cabinet?

The reason I am asking all of this is we are having a discussion here at work and I say they can and the other inspector is saying they can't.

I showed him this section and he stated that section doesn't cover the service panel. I said so.....the service panel isn't an enclosure for switches an overcurrent devices? He said.....No.....I said show me the section where you say it isn't allowed......he's still looking :)
 

iwire

Moderator
Staff member
Location
Massachusetts
The inspector needs to spend some time in Article 100.

A 'Panelboard' service or otherwise does not have an enclosure. A panelboard to the NEC is just the 'guts' As covered by Article 408

Panelboards are installed in cabinets as covered by Article 312.


Panelboard. A single panel or group of panel units designed
for assembly in the form of a single panel, including
buses and automatic overcurrent devices, and equipped
with or without switches for the control of light, heat, or
power circuits; designed to be placed in a cabinet or cutout
box
placed in or against a wall, partition, or other support;
and accessible only from the front.


Cabinet. An enclosure that is designed for either surface
mounting or flush mounting and is provided with a frame,
mat, or trim in which a swinging door or doors are or can
be hung.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Bob, hit the nail on the head. You need to know what the definitions before you can answer the question. :)
 