Pierre I do not think it is physically possible to fill a cross section of the panel beyond 75% fill with splices.Originally posted by pierre:
Jim says he sees this seldom, I see it quite a bit, even without the splices... NY must have smaller gutter space panels![]()
I had not noticed this until someone pointed it out to me the other day.312.8 Enclosures for Switches or Overcurrent Devices.
Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless adequate space for this purpose is provided. The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.
I read this to say that if the conductors terminate on a breaker in this same panel, this section does not apply.Originally posted by iwire:
While we are at this I do have a question.
Do we have to count conductors in this calculation that are not feeding through or tapping off to other switches or overcurrent devices?