david
Senior Member
- Location
- Pennsylvania
Not sure why you thought that, but the inverters really can't deliver fault current above their normal operating current. So they are basically a rounding error compared to the available fault current from the utility. With very large systems this might not be the case but even with 60kW all put together from the multiple units that's pretty much going to be the case here.
Actually I'm getting that Idea from Mike Holts Video
2014 NEC- Point of Conection To Utility Power [705.12] (1hr:28min:43sec)
I'm pretty sure he saying the buss rating must be sized to handle fault current from both sources additive