312.8 Switch and Overcurrent Device
Enclosures with Splices, Taps, and Feed-
Through Conductors
The wiring space of enclosures for switches or overcurrent
devices shall be permitted for conductors feeding through,
spliced, or tapping off to other enclosures, switches, or over-
current devices where all of the following conditions are
met:
(1) The total of all conductors installed at any cross section
of the wiring space does not exceed 40 percent of the
cross-sectional area of that space.
(2) The total area of all conductors, splices, and taps in-
stalled at any cross section of the wiring space does not
exceed 75 percent of the cross-sectional area of that
space.