I was wondering what approach you guys like to take when upgrading a ITE push a matic panel to a new loadcenter. In a push a matic panel, all the grounds and neutrals are terminated on the very top of panel which can make a real hassle when switching over to a standard loadcenter. How do you splice all neutrals, grounds and hots, or do you J box them outside the panel and bring new wire in? Also, Have you ever had inspectors frown on splicing in the panel to lengthen the conductors? THANKS!
As long you don't violate 75% fill he shouldn't have anything to frown about
312.8 Enclosures for Switches or Overcurrent Devices.
Enclosures for switches or overcurrent devices shall not be
used as junction boxes, auxiliary gutters, or raceways for conductors
feeding through or tapping off to other switches or
overcurrent devices,
unless adequate space for this purpose is
provided. The conductors shall not fill the wiring space at any
cross section to more than 40 percent of the cross-sectional
area of the space, and the conductors, splices, and taps shall
not fill the wiring space at any cross section to more than
75 percent of the cross-sectional area of that space.