dnbob
- Rochester, MN
Re: splicing of 500MCM
There are services and lugs that are 90c rated. (FYI)
Please ask him which manufacturersHe has told me that any gear now being manufactured above 100 amps has 90c rated lugs.
Seimens, and Square D are the only two I asked about...Remember this is still unconfirmed I have e-mails out to the engienners at both companiesOriginally posted by websparky:
Please ask him which manufacturersHe has told me that any gear now being manufactured above 100 amps has 90c rated lugs.![]()
No. Many wire connectors are suitable for use at 90?C, but often the equipment that the wire connectors are attached to is not listed for the higher temperature. You can't just look at the temperature rating of the wire connector, you have to look at the other information that has been provided by the equipment manufacturer.If it is UL listed gear with 90c lugs wouldn't that included all components of the switch gear?