None of which have a bearing on 240.4 so forget the distractions.
I thought you were a huge advocate of making the NEC 'right'? Here is a case where it may not be.
The situation we are discussing is a feeder in the form of a service-entrance conductors being tapped to smaller feeders, also service-entrance conductors.
230.46 Spliced Conductors. Service-entrance conductors shall be permitted to be spliced or tapped in accordance with 110.14, 300.5(E), 300.13, and 300.15.
None of the references in 230.46 aid this discussion.
I read the tap conductor definition to exempt service [entrance] conductors from the source side OCPD requirement that generally applies to tap conductors. This conforms to many multi-service installations containing 6 or less services.
240.2 Definitions.
Tap Conductors. As used in this article, a tap conductor is defined as a conductor,
other than a service conductor, that has overcurrent protection ahead of its point of supply that exceeds the value permitted for similar conductors that are protected as described elsewhere in 240.4.
iwire posited this section as the one governing the taps.
240.4 Protection of Conductors. Conductors, other than flexible cords, flexible cables, and fixture wires, shall be protected against overcurrent in accordance with their ampacities specified in 310.15,
unless otherwise permitted or required in 240.4(A) through (G).
as they are taps, section (E)(3) governs:
(E) Tap Conductors. Tap conductors shall be permitted to be protected against overcurrent in accordance with the following:
(3)
240.21, Location in Circuit
240.21(B) allows load end OCPD for taps which meet proper requirements.
240.21 Location in Circuit. Overcurrent protection shall be provided in each ungrounded circuit conductor and shall be located at the point where the conductors receive their supply
except as specified in 240.21(A) through (H). Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an overcurrent protective device meeting the requirements of 240.4.
(B) Feeder Taps. Conductors shall be permitted to be tapped,
without overcurrent protection at the tap, to a feeder as specified in 240.21(B)(1) through (B)(5). The provisions of 240.4(B) shall not be permitted for tap conductors.
For sake of argument I assume either tail of the 3/0 conductor does not exceed 7.5 m
(2) Taps Not over 7.5 m (25 ft) Long. Where the length of the tap conductors does not exceed 7.5 m (25 ft) and the tap conductors comply with all the following:
The maximum OCPD for 750kCMil CU 75?C conductor is the next higher standard size above 475A. Looking in 240.6 (A) I find that to be 500A. The maximum current rating for 3/0 CU 75?C conductor is 200A from 310.15(B)(16). Using the 500A value as the conservative choice I get 200/500 or 0.4 ratio. The required ratio is 0.33 so the (1) requirement is met.
(1) The ampacity of the tap conductors is [red]not less than one-third[/red] of the rating of the overcurrent device protecting the feeder conductors.
I assume this to be the case, information not provided.
(2) The tap conductors terminate in a single circuit breaker or a single set of fuses that limit the load to the ampacity of the tap conductors. This device shall be permitted to supply any number of additional overcurrent devices on its load side.
I assume this to be the case, information not provided.
(3) The tap conductors are protected from physical damage by being enclosed in an approved raceway or by other approved means.
I posit that the 3/0 conductor never carries more than a 200A OCPD will allow along its length, with the possible exception of a part in a 1 inch connector. I further claim that the suggestion of a total of 400A of OCPD ignores the geometry of the situation.