bill@enleyelectric.com
Good Morning,
I have a job that we are finishing up and ran into some trouble on my rough inspection. We have a mixed use old bldg (major university dorm/frat house area where all of the frat houses are old brown stones converted) that will be 8 studio apartments, a 3 br apartment and various meeting rooms / commercial kitchen / worship area.... I have dual 600 amp services; one single phase for the meter stack feeding the apartments and the other 3 phase serving all house loads and the commercial kitchen.
The plans called for a 3/0 GEC which we took continuosly from the cabinet of the single phase meter stack breaker, into our 3 phase CT cabinet where we lugged it to the 3 phase service neutral out of there to a 10' 3/4" rod, up to the top of the room where we lugged it to bldg steel, and then to the 2" copper water line at its point of entry to the bldg where we ended it in a water pipe clamp listed for such.
Two things: As the GEC traveled through our electrical room we bonded all of the cabinets/troughs to the GEC with the appropriatley sized conductor based on largest ungrounded conductor in that particular cabinet or trough (i believe 250.166 but im not in front of my code book), to teminate at the GEC we used split bolt connectors to attach to the unbroken GEC. My inspector wants those connections to be weld or crimp (is that correct??
He also wants me to crimp onto/extend the GEC at the incoming water service and then instead of ending the GEC at the water pipe, he wants me to extend it in its unbroken (now continuous crimped) length across the water meter/backflow preventer and then leave enough 3/0 so that when the gas equipment/meter is installed we can bold across that with this GEC also. Does this seem right? We did have the water meter bonded/jumpered indepently from the GEC. Is that jumper also sized according to the GEC size that he is requesting?:?
I love this forum, ive been a member for a long time and dont post much but read often.