In another thread, I made mention of proper termination on split bolts (number of wires). I could not confirm where I had been told that split bolt connectors were listed for "1 line-1 tap". I contacted T&B and received the follwing e-mail which I thought might be of interest to forumites.
"All testing and listing for UL requirements is done with only 2 conductors - one line and one tap.
It is possible other combinations may pass the requirements but we have no testing to verify this performance."
Byron Raines
Manager - Technical Services
Thomas & Betts
"All testing and listing for UL requirements is done with only 2 conductors - one line and one tap.
It is possible other combinations may pass the requirements but we have no testing to verify this performance."
Byron Raines
Manager - Technical Services
Thomas & Betts