I apologize for my unfamiliarity with this type of panel but they are rare in my area and I don't know much about them. I am not the installer or AHJ, but doing a third party certification of the PV system which includes the interconnection.
I am unsure if there any rules that apply to the bus on the supply side of the connection. Do the breakers (read: disconnects?) need to have the same interrupt rating that a mocpd would have? Am I missing anything regarding the bus bar loading? My first criteria would be to cite 705.12(A) that the ratings of the sum of all the supply side overcurrent devices not exceed the rating of the service (in this case the bus). Just trying to learn and I appreciate any insight the panel can offer.