Hi,
How would you apply the 120% Rule to a main panel with a split bus? Let's use a 400A main panel with a 200A/200A split bus for this example.
Would you have to distribute the OCPD's evenly? Ex: 40A PV breaker on one bus, and a 40A on the other?
Or could you just put all 80A on one bus?
Regards,
Andy