JoeNorm

Senior Member
Location
WA
I have a customer building a detached garage next to main house. Any reason I cannot find the service conductors to the main house in the ground, splice in another set to feed a 200a disconnect that goes to the new garage?

This allows either structure the 200a capacity. This assumes load calc allow for it but in this case it should.
 
Good question. I suppose the utility does, but these wires are on the metered side. In-between house and meter.
 
I have a customer building a detached garage next to main house. Any reason I cannot find the service conductors to the main house in the ground, splice in another set to feed a 200a disconnect that goes to the new garage?

This allows either structure the 200a capacity. This assumes load calc allow for it but in this case it should.
Sure, see 230.40 exception #3
 
Make sure you have a load calc for the total to make sure you're under 200 total and if it's 4/0 make sure you're at 180. If you do a small vault it'll have room for the taps too. Optional method will get the house load small.
 
One inspector here would ride any new house over 2000 ft^2 but he's doing virtuals now so lately he hasn't bugged me. He also was convinced that voltage drop was a serious problem in homes if there was over 100ft of wire. He's a character.
Voltage drop isn't a code rule, it's only an informational note.
 