Did a service call today, and found this gem in the basement:

DSC05956a.jpg
 
Now that I look at it again thats wood isn't it. Voilation of C also.

Faceplates of insulating material shall be noncombustible and not less than 2.54 mm (0.010 in.) in thickness
 
480sparky said:
Did a service call today, and found this gem in the basement:

DSC05956a.jpg

If the wire is #12 and the box is 18 cu" then:

NEC 2008 314.16 Number of Conductors in an Outlet, Device, and Junction Boxes, and Conduit Bodies.

Also: T314.16(B) Volume Allowance per Conductor
 
BackInTheHabit said:
If the wire is #12 and the box is 18 cu" then:

NEC 2008 314.16 Number of Conductors in an Outlet, Device, and Junction Boxes, and Conduit Bodies.

Also: T314.16(B) Volume Allowance per Conductor

Looks like there is just 2 cables and the NM feeding the bottom box routes around the first.


billsnuff said:
don't care for the 2 NM's under the staple......JMSO

You'd hate my work, then. :grin:

Edit to add:
Oh, yeah...hard to tell the "big picture" from the close-up pic, but I am not in favor of the NM stapled to the front edge of stud.
 
Pierre C Belarge said:
The receptacle may not be GFCI protected.

I ran two bath circuits to the two bathrooms today. House was built in the late 60s, so I bet the two GFIs I put in are the only two in the house.
 
What is
334.17 Through or Parallel to Framing Menbers, referring also to
300.4 (D) Cables and Raceways Parallel to Framing Members and Furring Strips, Alex?
 