Spot the violation

Merry Christmas
Status
Not open for further replies.
tom baker said:
Service conductors must be 3 ft above a window that opens.


, Thank You, I knew it was border line.


I wouldn't walk on them steps either, not at all.
The drip loop does not appear to be 10 ft. from the steps.
If the steps we're to code you may have a clearence issue with your panels.
 
Last edited:
tom baker said:
2" PVC, if thats what it is, requires support every 5 ft.
Service conductors must be 3 ft above a window that opens.

While my POCO wont allow it, the code will.
Exception: Conductors run above the top level of a window shall be permitted to be less than the 900-mm (3-ft) requirement.
 
stickboy1375 said:
What problem would that be? Siding guy is going to be happy!

My point was that if all the cables are going the same hole. the chances of multiple occupancy are slim.

I see a violation of article 230.2 and 230.71 in the picture.There are two service drops that are not parallel and there are more than 6 disconnects.
Rick
 
RUWired said:
My point was that if all the cables are going the same hole. the chances of multiple occupancy are slim.

I see a violation of article 230.2 and 230.71 in the picture.There are two service drops that are not parallel and there are more than 6 disconnects.
Rick

This amounts to two services so 230.71 won't apply. If the AHJ approves it I see no violation other than the strapping issue. 230.2(C)Ex.
 
infinity said:
This amounts to two services so 230.71 won't apply. If the AHJ approves it I see no violation other than the strapping issue. 230.2(C)Ex.

You can't see the can, but there is only one transformer feeding it.IMO, if the can is big enough to supply the 2 drops, then only one drop should have been put in, but that would now fall into poco territory.I only see one sticker on the right service equipment.I can't say if both were approved or what the reasoning for the two drops.
Rick
 