If nothing else, I'm going to say that this installation is outside. Are PVC MAs listed for wet locations when placed through a simple KO?
Yes...to your question.and now a phone call.....hello Carlon or whomever........yes greg.......hi I have question.......yes Greg.....Can I drill holes in one of your conduit bodies and install more raceways?.........I don't think so..... see for starters NEC 110.3(B) and we will send you more information if needed......thanks....goodbye. I am not being a smart a** but that is my point. And I am calling them as we speak. Violating their warranty / use is the key word.
Are you serious or just testing/teasign?:smile:
It is a fitting, not designed, nor designated for field fabrication.
I understand that per section 314.16(C) What I am trying to convey is altering the conduit body itself as a manufactured piece of equipment. Is it acceptable per the manufacturer????
I would contact the contractor and ask him to provide me with a letter from the manufacturer as to the validity of the installation.
So ,..I guess it is a violation1.17 Externally-threaded adapters (also referred to as terminal adapters) covered by these requirements are fittings intended for joining a length of rigid PVC conduit or elbow or other bend to:a) The knockout area of a metal box with a metal locknut,
b) A threaded metal hub or fitting on a metal box,
c) A threaded hub on a phenolic box, or
d) A knockout in a phenolic box.
So ,..I guess it is a violation
If you think this is OK, because the UL listing or manufacturer doesn't "tell" you that you can't make the modifications, then what would be the purpose of obtaining a UL listing for ANY product?
If the manufacturer does not specifically state what modifications may be done (if any), then it is safe to assume the modifications render the product not covered by the UL listing unless you paid for a UL field inspector to visit the job site, and evaluate the application and product modifications.
Is not possible to tell from picture ....but there may be a self sealing locknut inside of body?I have to agree, the MA is being used wrong.![]()
My point is that the wireway is tested to be NEMA or UL listed using the typical modifications that would be encountered (i.e. field drilling).
Serious.
Unless that is included with the listing of the equipment it is just an opinion.