Spot the Volation(s) 10/24/08

Status
Not open for further replies.
I?m going to go with:
314.15(A), round box cover ?shall be listed for use in wet locations.?
314.22, round box cover incorrectly used as extension from apparent flush box.
358.30(A), EMT fastening between condulets is missing.
 
I see the round plate only as flashing to cover a hole, it is missing some straps, but is the luminaire rated for exterior? My bad now I see the round plate is not a flashing it is a cover plate not rated for wet locations.
 
Last edited:
314.22 Exposed Surface Extensions.
Surface extensions from a flush-mounted box shall be made by mounting and mechanically securing an extension ring over the flush box. Equipment grounding and bonding shall be in accordance with Article 250.

Exception: A surface extension shall be permitted to be made from the cover of a flush-mounted box where the cover is designed so it is unlikely to fall off or be removed if its securing means becomes loose. The wiring method shall be flexible for a length sufficient to permit removal of the cover and provide access to the box interior, and arranged so that any bonding or grounding continuity is independent of the connection between the box and cover.
 