24 vdc bell the way I would do it in the past was to put a power eol at the flow switch to at least supervise from the panel to the switch,but I would like to figure out the proper way to suprvise the whole circuit.The plan was to run 24 volts from the panel go through the flow switch to the bell cant figure out how to supervise from switch to bell,addressable system.
So the Flow switch is activating the bell, its coming off the aux terminals on the panel. Right?
What do you propose to supervise the power, a monitor module with a relay that is powered, like a 4 wire smoke loop?
The technically correct way to perform supervision would be with a Addressable
Notification Module, not a "control/relay". You cannot properly supervise it on the other side of the WF switch.
A lot of guys just use a addressable relay. There is no way to supervise it that way.