Sprinkler head location

Status
Not open for further replies.

bgs1362

Member
Does the NEC prohibit sprinkler heads in switchgear rooms?

Are there any limitations as to location in switchgear rooms?
 

wwebb

Member
Re: Sprinkler head location

In the 2002 NEC, look up Article 110.26(F)(1)and check out a handbook for a little better explanation.
 

ryan_618

Senior Member
Re: Sprinkler head location

The IBC and the NFPA 13 does not allow eliminating a sprinkler head from an electrical room. If your building is required to be sprinklered, you will have one in your equipment room, like it or not.
 