B bgs1362 Member May 6, 2005 #1 Does the NEC prohibit sprinkler heads in switchgear rooms? Are there any limitations as to location in switchgear rooms?
Does the NEC prohibit sprinkler heads in switchgear rooms? Are there any limitations as to location in switchgear rooms?
W wwebb Member May 6, 2005 #2 Re: Sprinkler head location In the 2002 NEC, look up Article 110.26(F)(1)and check out a handbook for a little better explanation.
Re: Sprinkler head location In the 2002 NEC, look up Article 110.26(F)(1)and check out a handbook for a little better explanation.
ryan_618 Senior Member Location Salt Lake City, Utah May 6, 2005 #3 Re: Sprinkler head location The IBC and the NFPA 13 does not allow eliminating a sprinkler head from an electrical room. If your building is required to be sprinklered, you will have one in your equipment room, like it or not.
Re: Sprinkler head location The IBC and the NFPA 13 does not allow eliminating a sprinkler head from an electrical room. If your building is required to be sprinklered, you will have one in your equipment room, like it or not.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician May 6, 2005 #4 Re: Sprinkler head location The sprinkler piping can be in an electrical room, but not in the dedicated electrical space as described in 110.26.
Re: Sprinkler head location The sprinkler piping can be in an electrical room, but not in the dedicated electrical space as described in 110.26.