Does the NEC prohibit sprinkler heads in switchgear rooms?

Are there any limitations as to location in switchgear rooms?
 
Re: Sprinkler head location

In the 2002 NEC, look up Article 110.26(F)(1)and check out a handbook for a little better explanation.
 
Re: Sprinkler head location

The IBC and the NFPA 13 does not allow eliminating a sprinkler head from an electrical room. If your building is required to be sprinklered, you will have one in your equipment room, like it or not.
 
Re: Sprinkler head location

The sprinkler piping can be in an electrical room, but not in the dedicated electrical space as described in 110.26.
 