But does it need to be bonded based on the service size or the largest circuit most likely to energize the piping system 250.104 B 1 and in this case the only circuit in the vicinity would be 20 amp.
Doesn't that depend on were the Fire Pump is located? Generally the motor controller for the Fire Pump is service equipment. How close is that? There may also be a Fire Department Connection Siamese or manifold inlet which is usually metallic piping. If the Utility's Water Main in the street is metallic of otherwise conductive, such as reinforced concrete piping, it will provide a conductive path between the 2 water service lateral lines. The concern may be that many fire sprinkler supply laterals are being assembled with Victaulic Couplings. Those function as an insulating coupling. When the subway system was built in Washington DC the electricians had to bond around every Victaulic coupling. That was before I came there so I don't know why.
Tom Horne