I doubt many would agree.If you are addressing it as a grounding electrode then 3/0 is the largest required (250.66) and if you are bonding it then under '23, 3/0 again is the largest required.
But does it need to be bonded based on the service size or the largest circuit most likely to energize the piping system 250.104 B 1 and in this case the only circuit in the vicinity would be 20 amp.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
But does it need to be bonded based on the service size or the largest circuit most likely to energize the piping system 250.104 B 1 and in this case the only circuit in the vicinity would be 20 amp.
It's metal water piping so I would think 250.104(A),,,, service size.
 