Dan Mulligan
Member
But does it need to be bonded based on the service size or the largest circuit most likely to energize the piping system 250.104 B 1 and in this case the only circuit in the vicinity would be 20 amp.I doubt many would agree.If you are addressing it as a grounding electrode then 3/0 is the largest required (250.66) and if you are bonding it then under '23, 3/0 again is the largest required.