Im trying to find a good space heater for a small 5' x 5' sprinkler room attached to a row of townhouses. The existing space heater was only a 2ft baseboard heater 240v.
It needs to be tamper proof for the thermostat and atlease 2ft.
Any ideas?
this is an insurance job because someone gained access to this room and turned the heat up and caused the sprinkler to open....per the fire marshalls report.
Here's the fix from the property association.
Install a tamper proof thermostat and heater that is better suited for sprinkler room/commercial area.
someone gained access to this room
:roll:2' residential baseboard heater got the room to 180 degrees and popped a sprinkler
Hold the phone there Gracie
We don't have these kind of problems here, but why didn't the sprikler installers just wrap the pipe with a pipe heater?
...someone gained access to this room and turned the heat up and caused the sprinkler to open....per the fire marshalls report.
The stupidity of this finding can't be described with words.
I would not let someones stupidity keep me from making money.
I have to say I have never seen that done, I see plenty of other kinds of pipes heat traced but never sprinkler pipes.
We typically use fan forced electric unit heaters in sprinkler rooms.
If the sprinkler pipes are going to be in unheated areas they will either install a dry system or use glycol in the lines.
Im trying to find a good space heater for a small 5' x 5' sprinkler room attached to a row of townhouses. The existing space heater was only a 2ft baseboard heater 240v.
It needs to be tamper proof for the thermostat and atlease 2ft.
Any ideas?
Like I said don't have those problems here.
Well then I guess my next question would be, do you really need to put in a heater that goes up to 180 degrees.
We typically use fan forced electric unit heaters in sprinkler rooms.
.
Hold the phone there Gracie - You're telling me that a 2' residential baseboard heater got the room to 180 degrees and popped a sprinkler?
That Fire Marshal, while possibly not a moron, is certainly inept.
db
I have gone on a couple of calls were a sprinkler line froze and flooded areas. Glad I did not have to clean it up. :grin: