Whats wrong with a heat detector in the room?
Whats wrong with a heat detector in the room?
Well, unless its tied into the heater, whats the point? The sprinkler head popped, not a smoke. Adding a heat detector to shut down the unit I assume you meant?
I'm curious why the t-stat needs to be tamperpoof. With a room that small I can't imagine that there is anything other then the riser in there, in which case the door might get opened once a year. Who's going to tamper with it?
In regards to your heaters. I like to install two heaters in that situation on seperate circuits. The t-stats get set at 50 and 40 degrees. It serves two purposes. ONE if the first heater can't keep up ona really cold night the second makes up the differance. TWO if one fails and trips a circuits the second one takes over. Assuming this room will only be visited one a year for an inspection, how is anyone acutally going to discover that the heaters aren't working?
this is an insurance job because someone gained access to this room and turned the heat up and caused the sprinkler to open....per the fire marshalls report.
Here's the fix from the property association.
Install a tamper proof thermostat and heater that is better suited for sprinkler room/commercial area.
A RoR heat should trip before that sprinkler head ops. I suppose you could shut down the heater but if the heat goes off and the dialer calls out there will be people there soon enough.