Can anyone tell me if a sprinkler room is considered a wet location?
I know the wiring methods to a fire pump motor needs to be IMC rigid or seal tight. I am OK with that, but I have an inspector telling me the whole room is a wet location so all wiring needs to be rated for wet location.
We replaced an existing fire pump and controller using existing wiring. There is a generator feed to the controller that is EMT with set screw connectors and he want the connectors changed to compression along with a few other conduits.
I know the wiring methods to a fire pump motor needs to be IMC rigid or seal tight. I am OK with that, but I have an inspector telling me the whole room is a wet location so all wiring needs to be rated for wet location.
We replaced an existing fire pump and controller using existing wiring. There is a generator feed to the controller that is EMT with set screw connectors and he want the connectors changed to compression along with a few other conduits.