Would the fact that I have a sprinkler system (for fire) in a warehouse mean that all electrical panels and equipment in that warehouse have to be NEMA 3R?
Would the fact that I have a sprinkler system (for fire) in a warehouse mean that all electrical panels and equipment in that warehouse have to be NEMA 3R?
No. A sprinkler system installed within an electrical closet/room does not change the classification of the room to a "wet location". The classification of the warehouse is regulated by the materials stored within.
Location, Dry.
A location not normally subject to dampness or wetness. A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction.