Re: Sq-D Generator Interlock
There are 7 differnet generator interlock kits for SquareD panels plus the QO2DTI. Please download the installation directions from
www.squared.com.
For 150 amp amd 200 amp main breaker panels:
RCGK2 and QCGK2 are for the combination service entrance devices and for similar outdoor panels that have a lift up door or a lift and turn door. These are also for the indoor panels.
QORBGK2 and HOMRBGK2 are for the outdoor panels that have a side hinged door.
For the 100 amp 8 slot panels that have a single row of circuit breakers you would use the QO2DTIM which contains the QO2DTI puls 2 main breaker retainers. This secures two 2 pole back fed main breakers.
For 100 amp and 125 amp main lug convertible load centers that have 2 vertical columns of circuit breakers:
PK4DTIM4LA and PK4DTIM4LAL which secure 2 back fed breakers up to 125 amps each provided that you have enough wire bending space for 110 amps or 125 amps.
For 150 to 225 amp main lug load centers that are derated to 100 or 125 amps use the PK4DTIM4HA kit. This secures 2 back fed main breakers.
Mike Cole,
Sorry about my spelling at 5 a.m.