by sawing (or some way cutting) the left neutral bar loose from the factory tie bar they have already altered the listed panel in such a way that nothing you do short of a replacement would allow the job to pass inspection here.
The question to ask the OP now: Does the meter box have an integral disconnect (meter/main)? Or is it configured they way you suggested with both the ground and neutral wires stuffed into the same lug?
So everything is bonded at the service disconnect.
Looks to me like all you need to do is take all the ground wires in the circuit panel and bond them to the cabinet via installing a new ground bar and a ground lug if still necessary..
Am I missing something?
Aha! One of my conclusions was correct.... there should have been an exterior disconnect installed.
Got to love the 2 conductors under 1 lug, and 1 conductor under 2 lugs. That's just priceless.:roll:
Yes, there is, and no, they coiuldn't. Everything past the main disconnect must be wired with separate neutral and EGC, whether the main is first, as in this example, or within the breaker panel itself.Just out of curiosity, is there a code requirement for the 3/C insluated with bare gnd going from the outdoor disconnect to the main service panel? It would seem they could have continued with the 2 insulated conductors and the bare ungrounded conductor to the main service panel?
Yes, there is, and no, they coiuldn't. Everything past the main disconnect must be wired with separate neutral and EGC, whether the main is first, as in this example, or within the breaker panel itself.
In other words, if you understand the requirement as it applies to branch circuits, or better yet, to sub-panels, having a separate main disconnect like this one renders the breaker panel a sub-panel.