Square D 100 Amp Main

Status
Not open for further replies.

C3PO

Senior Member
Location
Tennessee
The picture Dennis posted is that of a Q12100TF (as in top feed). It went across the entire width of the panel and the conductors entered the 'side' of the breaker. Replacing this with a standard QO2100 is possible except your incoming line conductors will probably not be long enough.

When the Q12100 was obsoleted, back in the 80's, it was replaced with the QO2100. I do not recall that a QO2100TF was ever produced unless it was as a special 'form and fit' replacement.

In the old style panels the neutral bar would not be in the way, it would have been located at the end of the panel, usually between the breaker lugs.

I was hopeing you would chime in. You have forgotton more about Square D and it's "product history" then I will ever know. :smile:
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
one supplier is mentioning a kit SQ D # Fk5-669 to convert
Someone is wrong.

The part number would be an SK5669, but it was used only in panelboards never in loadcenters. Even then, it was never required for replacement purposes.
 