Just performed a 200 A service upgrade....first one on my own with my license
. In any case, the customer wanted a square D Homeline Panel. This particular panel had an odd setup compared to the Murray panels that I'm used to using. Above the main disconnect, were the two terminals for the ungrounded conductors. In between these two terminals, was the terminal for the grounded conductor and directly adjacent to the this terminal (immediately to the right of it (in fact they were cast together)) was a smaller terminal which i can only imagine was for the Grounding Electrode Conductor. Installed on either side of the panel were ground bars. I installed the grounded conductor and G.E.C. in the appropriate terminals and bonded the neutral/ground bus and bonding strip to the cabinet itself with the green bonding screw. My question is.....do the ground bars on either side of the panel require additional wiring to effectively ground the egc's? (such as running the equivalent of the largest sized egc to that ground bar from the neutral/ground bus........as you would if you were installing a ground bar in say a separate trough)....does the use of the bonding screw make this unnecessary? Also, Does anyone know why square d uses this set up? Is it so the panel can be readily used as a sub-panel?
Any insight is always appreciated