All I can say is this company been making them that way since the late 1960's and new systems today still use a grounded conductor as the "safety circuit" for the main control. Any limit throughout the system will interrupt the return portion of this grounded conductor. It runs all the way to end of the system, all intermediate motor contactors connect to it as a "common", but then a return conductor has all the safety limits in it on the way back to the main control panel. Back there it ties to the holding contacts on the main contactors. Start button bypasses the holding contact and allows the system to run while holding start button, this is how you get it back "in line" if it stopped because it was out of line. Of course you need to fix whatever caused it to get out of line or if you hold it too long it just gets further out of line, possibly until something breaks.
Newer systems in recent years have gone to a "safety relay" and changed some things a bit, but that is all within the main control panel, out on the system the same number and colors of conductors haven't changed from day one and the grounded conductor is still where this safety circuit is tied to at far end then it comes back to the main control panel through all the limit switches.
I don't know what listing requirements may be, pretty certain these units are listed though.