Does anyone happen to know what the interrupting rating is for a Square D Mag Gard FHP Motor Circuit Protector (MCP) breaker? From looking at the Mag Gard FHL breaker which has an interrupting rating of 25kA I would venture to guess that the FHP breaker had the same rating since the only difference with the P vs the L refers to the mechanical connection of the breaker?
These FHP breaker are being used as part of combination starters located in a Square D Model 6 MCC. The Short Circuit Rating on the front of the MCC said that it was rated for 42kAIC, however these FHP breakers may only be rated for 25kA. Would the overall rating of the MCC then be 25kAIC since these FHP breakers are only rated for 25kA?
What is an MCC does not have any information on the front in regards to the short cirucit rating? Do you simply have to go off of the lowest rated breaker installed in the MCC?
These FHP breaker are being used as part of combination starters located in a Square D Model 6 MCC. The Short Circuit Rating on the front of the MCC said that it was rated for 42kAIC, however these FHP breakers may only be rated for 25kA. Would the overall rating of the MCC then be 25kAIC since these FHP breakers are only rated for 25kA?
What is an MCC does not have any information on the front in regards to the short cirucit rating? Do you simply have to go off of the lowest rated breaker installed in the MCC?