schwarz633
Member
- Location
- WI
In order to accommodate a portable generator circuit and mechanical manual interlock I'm installing a 200A main lug only QO 40 space panel next to my existing 200A main breaker 40 space panel, as I need additional breaker spaces. I will be powering the sub panel from a 2-pole 100A breaker in the main panel. As best I can determine, the largest conductor the neutral/ground bar in the main panel will accept is #4. The smallest conductor the 100A 2-pole breaker will accept is #4. The smallest conductor the sub panel main lugs will accept is #6. I have a 1-1/2" rigid nipple between the panels. So I guess I will be using (3) #4 THHN and (1) #8 ground, does that sound right? Am I correct in my understanding that the sub panel load side conductors may not pass through the main panel?