srapping mc for a 2X4 fixture

Status
Not open for further replies.
Re: srapping mc for a 2X4 fixture

Not always.

330.30(B) Unsupported Cables. Type MC cable shall be permitted to be unsupported where the cable:

(2)Is not more than 1.8 m (6 ft) from the last point of support for connections within an accessible ceiling to luminaire(s) [lighting fixture(s)] or equipment
 