Saw a service today as follows:
Underground 200A service to the meter pedestal. Out of the back of the meter pedestal through the sill plate with 2" FMC. FMC runs about 3' to a 12" x 12" j-box. 2" EMT runs from down from there into the panel. Main breaker is in the panel.
Neutral is bonded to the meter can. The service conductors are spliced in the 12" x 12" j-box with Polaris connectors, and the j-box is labeled as "Line side tap location for future solar service." A #4 green wire is brought up to a small ground bar in the j-box (presumably for future solar interconnection) from the panel's ground bar. N-G bond is in the main panel via the green bonding screw. Ufer ground and water bond land in the panel as well.
I was asked if #4 supply-side bonding jumper (correct terminology?) should accompany the service conductors through the FMC out to the meter pedestal? If yes, what purpose would it serve, with the meter pedestal being bonded to neutral, and the EMT / #4 bonding the j-box from the panel-end? Where to land the bonding jumper in the meter pedestal?
My contention is that the service is fine as installed; FMC isn't listed as a bonding/grounding means, the neutral connection to the meter can bonds it, and G & N are properly bonded at exactly one point in the panel (first means of disconnect). The j-box and EMT are properly bonded by the #4 wire to the j-box ground bar, as there are concentric KO's on the panel-end of the EMT run, but the j-box is field-punched at 2".
What say you all?
SceneryDriver
Underground 200A service to the meter pedestal. Out of the back of the meter pedestal through the sill plate with 2" FMC. FMC runs about 3' to a 12" x 12" j-box. 2" EMT runs from down from there into the panel. Main breaker is in the panel.
Neutral is bonded to the meter can. The service conductors are spliced in the 12" x 12" j-box with Polaris connectors, and the j-box is labeled as "Line side tap location for future solar service." A #4 green wire is brought up to a small ground bar in the j-box (presumably for future solar interconnection) from the panel's ground bar. N-G bond is in the main panel via the green bonding screw. Ufer ground and water bond land in the panel as well.
I was asked if #4 supply-side bonding jumper (correct terminology?) should accompany the service conductors through the FMC out to the meter pedestal? If yes, what purpose would it serve, with the meter pedestal being bonded to neutral, and the EMT / #4 bonding the j-box from the panel-end? Where to land the bonding jumper in the meter pedestal?
My contention is that the service is fine as installed; FMC isn't listed as a bonding/grounding means, the neutral connection to the meter can bonds it, and G & N are properly bonded at exactly one point in the panel (first means of disconnect). The j-box and EMT are properly bonded by the #4 wire to the j-box ground bar, as there are concentric KO's on the panel-end of the EMT run, but the j-box is field-punched at 2".
What say you all?
SceneryDriver