YesAren't those two green conductors main bonding jumpers?
That’s what I was kind of thinking but the service neutral is also connected so isn’t there already a fault current return path?Definitely needed !
But there is a System Bonding jumper in each service disconnect connecting the Isolated bar.The service neutral appears to be connected to an isolated neutral bar...not bonded without the green conductor.
That is common in transfer switches which may or may not be service equipment.
What "Service Disconnect" are you referencing. The Transfer switches. which are your service disconnects, have isolated neutrals and your green jumper is the MBJ.But there is a System Bonding jumper in each service disconnect connecting the Isolated bar.
I was confused on the bottom feed only as well. Although it came with a hole to mount the hub on top with too. This meter can has a sticker showing made back in 2002 I believe.This setup illustrates the advantage of using PVC nipples in this case. The meter neutral is bonded to the can and the discos have a main bonding jumper. Nothing else needs to be done.
I note, however, that the meter can appears to be an under ground feed ONLY as there is a label indicating so. This looks like it has created wire space rules violation as a result. That would get a fail in my book.
That’s what I’m referring to and that because of the green jumper the neutral is bonded to the chassis eliminating the redundant green wire going from meter can to service disconnect.What "Service Disconnect" are you referencing. The Transfer switches. which are your service disconnects, have isolated neutrals and your green jumper is the MBJ.
That’s what I’m referring to and that because of the green jumper the neutral is bonded to the chassis eliminating the redundant green wire going from meter can to service disconnect.
The MBJ must be within the service disconnect enclosure and is correct as shown. You can not use a SSBJ to the meter in this setup as the neutral is bonded in the meter can and would create a violation as you would be intentionally creating a parallel neutral path. Nor could you could use a SSBJ in lieu of the MBJ in the disconnect due to the requirement that the MBJ be within the disconnect enclosure.That’s what I’m referring to and that because of the green jumper the neutral is bonded to the chassis eliminating the redundant green wire going from meter can to service disconnect.
For the meter base, yes: the neutral is bonded to the can, making it part of the neutral, just like SUSE-only mains.That’s what I was kind of thinking but the service neutral is also connected so isn’t there already a fault current return path?