ctaylo360860
Senior Member
- Location
- colorado
- Occupation
- ME
I have a single phase 240/120 400 amp supply coming from poco transformer to my tap box. They ran 3-500mcm copper supply conductors. I plan to tap off the supply conductors to two 200 amp single phase panels using 3/0 copper conductors.
I’m looking at exhibit 250.12 and want to make sure I’m sizing my bonding jumpers and correctly Installing my gec.
The tap box needs to have a supply-side bonding jumper. Poco supplied 500mcm copper from transformer, and I have two sets of 3-3/0 copper conductors.
Should I size my Ssbj based on the poco conductors or my largest service conductors?
If it’s poco I need to run 1/0 cu from grounded conductor tap to the lug on my tap box.
If based on 3/0 being the largest I should be able to run #4 copper.
The picture in exhibit 250.12 shows the gec going to the tap box neutral.
Is that the only way, or Can I run #6 cu from each service disconnect out to two ground rods at each building? The buildings don’t have metal water pipe or ufer.
Also looks like I need to use 10ft ground rods since they will be going inside of the concrete sidewalk?
I’m looking at exhibit 250.12 and want to make sure I’m sizing my bonding jumpers and correctly Installing my gec.
The tap box needs to have a supply-side bonding jumper. Poco supplied 500mcm copper from transformer, and I have two sets of 3-3/0 copper conductors.
Should I size my Ssbj based on the poco conductors or my largest service conductors?
If it’s poco I need to run 1/0 cu from grounded conductor tap to the lug on my tap box.
If based on 3/0 being the largest I should be able to run #4 copper.
The picture in exhibit 250.12 shows the gec going to the tap box neutral.
Is that the only way, or Can I run #6 cu from each service disconnect out to two ground rods at each building? The buildings don’t have metal water pipe or ufer.
Also looks like I need to use 10ft ground rods since they will be going inside of the concrete sidewalk?