SSBJ sized using 250.102(c)(1)

Merry Christmas
Status
Not open for further replies.

ctaylo360860

Senior Member
Location
colorado
Occupation
ME
I have a single phase 240/120 400 amp supply coming from poco transformer to my tap box. They ran 3-500mcm copper supply conductors. I plan to tap off the supply conductors to two 200 amp single phase panels using 3/0 copper conductors.
I’m looking at exhibit 250.12 and want to make sure I’m sizing my bonding jumpers and correctly Installing my gec.

The tap box needs to have a supply-side bonding jumper. Poco supplied 500mcm copper from transformer, and I have two sets of 3-3/0 copper conductors.
Should I size my Ssbj based on the poco conductors or my largest service conductors?
If it’s poco I need to run 1/0 cu from grounded conductor tap to the lug on my tap box.
If based on 3/0 being the largest I should be able to run #4 copper.
The picture in exhibit 250.12 shows the gec going to the tap box neutral.
Is that the only way, or Can I run #6 cu from each service disconnect out to two ground rods at each building? The buildings don’t have metal water pipe or ufer.

Also looks like I need to use 10ft ground rods since they will be going inside of the concrete sidewalk?
 

Attachments

  • IMG_0509.jpeg
    IMG_0509.jpeg
    70.3 KB · Views: 16
  • IMG_0510.jpeg
    IMG_0510.jpeg
    70.4 KB · Views: 15
  • IMG_0511.jpeg
    IMG_0511.jpeg
    75.6 KB · Views: 15
  • IMG_0512.jpeg
    IMG_0512.jpeg
    116.2 KB · Views: 15
  • IMG_0513.jpeg
    IMG_0513.jpeg
    106 KB · Views: 15

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I almost asked this question a while back so you can read it for yourself. It appears that you would size it to the 2- 3/0 conductors

 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Depending on where the service point is you would size off either the 500 MCM conductors or the combined cross section of the (2) 3/0 and the answer is 1/0 either way. It's the same for your GEC, if you're landing here, unless it's just going to rods..

10ft ground rods are not required anywhere by the NEC.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
So looks like I need to run #6 from each service disconnect to- 2 ground rods at least six feet apart, and I can use a #4 as my ssbj from grounded conductor to the enclosure?

Yes. If you're also putting the GEC here, maybe replace that 4-port polaris with a 5-port one so that you can connect the SSBJ and GEC both directly to the grounded conductor.
 

ctaylo360860

Senior Member
Location
colorado
Occupation
ME
I guess if you are saying that because of the sidewalk an 8ft ground rod can't be put into the soil a full 8ft then yes, a 10ft ground rod could solve that.
Okay so I need a 1/0 ssbj from grounded conductor tsp to enclosure to make sure my enclosure is bonded.
 

Attachments

  • IMG_0515.jpeg
    IMG_0515.jpeg
    235.2 KB · Views: 5

ctaylo360860

Senior Member
Location
colorado
Occupation
ME
Yes. If you're also putting the GEC here, maybe replace that 4-port polaris with a 5-port one so that you can connect the SSBJ and GEC both directly to the grounded conductor.
I thought about this, and this maybe the way to go… i need to get project going and supply house took forever last time I ordered Insulated taps.
Is it a problem to run the gec from each service disconnect.
Basically the metal tap box is bonded to the grounded conductor via 1/0 ssbj enclosure lug and tap lug.
Both service conductors should be bonded via green screw in enclosure

Each service disconnect will have its own #6 gec and two ground rods
 

ctaylo360860

Senior Member
Location
colorado
Occupation
ME
I thought about this, and this maybe the way to go… i need to get project going and supply house took forever last time I ordered Insulated taps.
Is it a problem to run the gec from each service disconnect.
Basically the metal tap box is bonded to the grounded conductor via 1/0 ssbj enclosure lug and tap lug.
Both service conductors should be bonded via green screw in enclosure

Each service disconnect will have its own #6 gec and two ground rods
Something like this at each buildings service disconnect.
 

Attachments

  • IMG_0516.jpeg
    IMG_0516.jpeg
    737.6 KB · Views: 8
  • IMG_0517.jpeg
    IMG_0517.jpeg
    728.9 KB · Views: 8

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Yes, you can run separate GECs from each panel. For example, they could meet at the first rod, and then one could continue as bonding jumper to the second rod.

No undeground water pipe in this building?
 

ctaylo360860

Senior Member
Location
colorado
Occupation
ME
Yes, you can run separate GECs from each panel. For example, they could meet at the first rod, and then one could continue as bonding jumper to the second rod.

No undeground water pipe in this building?
So I had planned on running two separate gecs from each service to two sets of ground separate ground rods. The picture I posted is an example at one of the services…
 

ctaylo360860

Senior Member
Location
colorado
Occupation
ME
I see no problem with what you plan.
(You do need your bond screw in each panel)
Yeah tap enclosure should be bonded via 1/0 copper from grounded lug to lug on tap enclosure,both service panels are bonded via green screw and have a gec to grounds rods rom each service.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Ok if there's only one connection to the poco it's still one service. But since you have service panels on each building then yes, separate GECs and electrodes at each building, going to each service panel. All kosher.
 

ctaylo360860

Senior Member
Location
colorado
Occupation
ME
Thank you for the in depth and speedy replies truly appreciate you! Best way would have been to 5 port it and only pound one set of ground rods! After getting these 10 footers I may go that route if I can get them quick.
Meant from each service disconnect. Can’t edit my post now
 
Last edited:

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Doesn't matter what they ran inside the building (although you're supposed to bond if metal). If the underground water pipe to the building is metal it's considered an electrode and you're supposed to use it.
 