I have a single phase 240/120  400 amp supply coming from poco transformer to my tap box. They ran 3-500mcm copper supply conductors. I plan to tap off the supply conductors to two 200 amp single phase panels using 3/0 copper conductors.
I’m looking at exhibit 250.12 and want to make sure I’m sizing my bonding jumpers and correctly Installing my gec.
The tap box needs to have a supply-side bonding jumper. Poco supplied 500mcm copper from transformer, and I have two sets of 3-3/0 copper conductors.
Should I size my Ssbj based on the poco conductors or my largest service conductors?
If it’s poco I need to run 1/0 cu from grounded conductor tap to the lug on my tap box.
If based on 3/0 being the largest I should be able to run #4 copper.
The picture in exhibit 250.12 shows the gec going to the tap box neutral.
Is that the only way, or Can I run #6 cu from each service disconnect out to two ground rods at each building? The buildings don’t have metal water pipe or ufer.
Also looks like I need to use 10ft ground rods since they will be going inside of the concrete sidewalk?