- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
The secondary conductors of a step-down transformer will include an SSBJ sized per 250.102(C). Where are the two ends of that conductor terminated?
The secondary conductors of a step-down transformer will include an SSBJ sized per 250.102(C). Where are the two ends of that conductor terminated?
Can't you alternately bond the neutral in the disconnect and omit the SSBJ as shown?
Well, no, not exactly. The SSBJ is still required, although it's permitted to be a raceway or bus. And, you're supposed to move the GEC to the disconnect then, too. See 250.30(2) and (5).Can't you alternately bond the neutral in the disconnect and omit the SSBJ as shown?
There is an exception in 250.30(A)(2) where under specific conditions the SSBJ can be omitted on outside transformers but generally as jaggedben states the SSBJ is required.Can't you alternately bond the neutral in the disconnect and omit the SSBJ as shown?
Let's label (the the bond the neutral) the system bonding jumper ((SBJ) in your question.Can't you alternately bond the neutral in the disconnect and omit the SSBJ as shown?
SSBJ was never included in any transformers i wired up, but after determining its size as you said to 250.102 C, I connected mine at the transformer EGC BUSS OR metal eclosure and other end to disconnect panel EGC buss or metal enclosureThe secondary conductors of a step-down transformer will include an SSBJ sized per 250.102(C). Where are the two ends of that conductor terminated?
If the transformer is located outside, then i believe the grounding electride conductor must be made at the source transformer. I think in this situation the system bonding jumper would also be located here. This was a confusing for me as wellLet's label (the the bond the neutral) the system bonding jumper ((SBJ) in your question.
Your not being told that the SBJ cannot be moved to the first disconnect in the illustration if you choose to.
What would be "omitted" in the transformer would be the system bonding jumper and the grounding electrode system @ the transformer location
Because you moved them to the disconnect location
That's why as I believe your aware 250.30 (5) grounding electrode conductor "This connection shall be made at the same point on a separately derived system where the system bonding jumper is connected".
Post # 6If th
If the transformer is located outside, then i believe the grounding electride conductor must be made at the source transformer. I think in this situation the system bonding jumper would also be located here. This was a confusing for me as well
When the transformer XO is bonded and the required grounding electrode installed outside, you would want the grounded conductor to be the only bonded metal path from the transformer to the building.There is an exception in 250.30(A)(2) where under specific conditions the SSBJ can be omitted on outside transformers but generally as jaggedben states the SSBJ is required.
Yes one of my grounding and bonding books mentioned the grounded conductor could fulfill multiple roles as the SSBJ and grounded neutral conductor if sized for the larger of either.Post # 6
When the transformer XO is bonded and the required grounding electrode installed outside, you would want the grounded conductor to be the only bonded metal path from the transformer to the building.
Added bonded at the transformer, system bonding jumper at the building, grounded conductor bonded in two location
This is what I meant. Moved, not eliminated.Your not being told that the SBJ cannot be moved to the first disconnect in the illustration if you choose to.
What would be "omitted" in the transformer would be the system bonding jumper and the grounding electrode system @ the transformer location
Because you moved them to the disconnect location
First of all I misspoke in the above reply.Post # 6
When the transformer XO is bonded and the required grounding electrode installed outside, you would want the grounded conductor to be the only bonded metal path from the transformer to the building.
Added bonded at the transformer, system bonding jumper at the building, grounded conductor bonded in two location
250.30 (C) outside sourceYes one of my grounding and bonding books mentioned the grounded conductor could fulfill multiple roles as the SSBJ and grounded neutral conductor if sized for the larger of either.
However, it also said a separate SSBJ could be ran with the grounded conductor as long as a parallel path for objectionable current wasnt created - the earth ground rods path not counting as a path.
I would think under the method with a SSBJ and a grounded conductor, the source would have a system bonding jump and the first point of disconnect would not or vise versa but maybe not both.
This is what puzzled me in the past and I made many post here about this. If you are doing work in a breaker panel which is the first disconnect after the transformer secondary (previously instalked by someone else) but see no system bonding jumper to bond the neutral bus and ECG in the breaker panel are you to assume one was placed in the outside separetly derived transformer?
Or do you risk the violation of installing a redundant system bonding jumper at the first disconnect if there was one unknowingly alrrady installed in the upstream transformer (in door or out doors?)
Yes that means the disconnect and over current protection for the feeder supply would be at the transformer location or at a pedestal type location and the building feeder supply would have a neutral and a equipment ground from the feeder disconnect to the buildingWith an outdoor transformer I think it is important to address the exceptions:
250.30(A)(1) System Bonding Jumper
Exception No. 2: If a building or structure is supplied by a feeder from an outdoor separately derived system, a system bonding jumper at both the source and the first disconnecting means shall be permitted if doing so does not establish a parallel path for the grounded conductor. If a grounded conductor is used in this manner, it shall not be smaller than the size specified for the system bonding jumper but shall not be required to be larger than the ungrounded conductor(s). For the purposes of this exception, connection through the earth shall not be considered as providing a parallel path.
and if you take advantage of that exception
250.30(A)(2) Supply Side Bonding Jumper
Exception: A supply-side bonding jumper shall not be required between enclosures for installations made in compliance with 250.30(A)(1), Exception No. 2.
No, the outdoor tap rule for transformer secondaries (240.21(C)(4)) would allow the OCPD to be at the building supplied, outside or inside nearest the point of entry. The result is that the feeder consists only of the circuit conductors, with the grounded conductor as the fault clearing path.Yes that means the disconnect and over current protection for the feeder supply would be at the transformer location or at a pedestal type location and the building feeder supply would have a neutral and a equipment ground from the feeder disconnect to the building
I'm a little late to the discussion, but it seems to me that other than the outdoor transformer case just discussed, there's always an SSBJ between the enclosures of the transformer and the first disconnect. Moving the SBJ (from one enclosure to the other) doesn't change that.This is what I meant. Moved, not eliminated.
Knowing that there are different kinds of separately derived systems. For the exception to apply the building supply would have to be a feeder. That applies to a generator or a transformer or whatever the derived source might be.No, the outdoor tap rule for transformer secondaries (240.21(C)(4)) would allow the OCPD to be at the building supplied, outside or inside nearest the point of entry. The result is that the feeder consists only of the circuit conductors, with the grounded conductor as the fault clearing path.
Cheers, Wayne